Post by cathoderay on Jun 7, 2021 7:58:35 GMT
Hi all. I am starting out self employed. It's taking a bit of getting used too! Got a question about a megaflo direct. It's starting making a puff of high pressure water in the morning from the taps. I've recharge the air gap (twice). Everything looks OK with the cylinder. Not sure where to go next. Any ideas please? Thanks. Ray
|
|
|
Post by tomplum on Jun 7, 2021 8:57:21 GMT
Hello Cathodayray have you any auto air vents on the system, It could be dragging air in from one of those,
|
|
|
Post by cathoderay on Jun 7, 2021 9:55:21 GMT
Hi Tom. Thanks for your help. I'll take a look when I'm round there next. Tbf. If the airgaps recharged and the safety valves are operating correctly I think I will advise the cust. To wait and see...
|
|
|
Post by crowsfoot on Jun 7, 2021 18:43:09 GMT
I've not done much on mega-flows catho ,however, I'd have a look at the pressure reducing valve and also see if the filter needs a clean, beyond this I don't really know what else could be causing the early morning pressure surge?
|
|
|
Post by dickpuller on Jun 8, 2021 5:30:40 GMT
As my learned friend CF has stated, try the Inlet Group first, check replacements are available from MrCH. The other thing is the Buffer can disintegrate on these units. But lack of expansion area would generally result in discharge from the T&P valve.
|
|
|
Post by cathoderay on Jun 8, 2021 12:26:36 GMT
Thanks guys, I will do as advised. Ray
|
|
|
Post by cathoderay on Jun 11, 2021 14:02:48 GMT
No fault found. Ended up calling megaflo. They said it happens sometimes. "One of those things" !
|
|
|
Post by tomplum on Jun 11, 2021 16:28:18 GMT
Thanks for getting back Cathoderay, ' one of those things' they never mention on the sales pitch, every day is a skool day,,
|
|