Post by Deleted on Feb 13, 2016 19:13:12 GMT
Attachment DeletedThe picture shows two added manifolds to the main flow and return as this was for a big extension on a house needing four more rads. Microbore is good stuff if used and installed properly as you can't just tee into the 10mm for a feed for another rad because of the small flow rate but if used right no problems.
|
|
Deleted
Deleted Member
Posts: 0
|
Post by Deleted on Feb 13, 2016 19:18:38 GMT
This picture is where I started testing all my pipe runs as the chippys went through my pipe work 3 times and on site no one cares, you'll always be the one to blame if there is a leak even if its someone else's nail or screw through your work so always check it. Attachment Deleted
|
|
Deleted
Deleted Member
Posts: 0
|
Post by Deleted on Feb 13, 2016 19:24:18 GMT
|
|
Deleted
Deleted Member
Posts: 0
|
Post by Deleted on Feb 13, 2016 19:32:18 GMT
|
|
|
Post by battle1066 on Feb 13, 2016 19:34:10 GMT
Looks an nice install there PB neat and tidy.
The house I live in has 10mm micro bore - gives no issues but I would of preferred 1/2 copper.
My pet hate with this micro bore is it has no give - kinks just looking at it when removing the rad for decorating,unless I'm just too rough.
|
|
Deleted
Deleted Member
Posts: 0
|
Post by Deleted on Feb 13, 2016 20:23:37 GMT
You're to rough battle.
|
|
|
Post by battle1066 on Feb 13, 2016 20:26:35 GMT
You're to rough battle. PB. That's the same line our lass use you could be right
|
|
|
Post by welshplumber77 on Feb 16, 2016 21:29:27 GMT
hi pb, just wondering if it would be possible to tee into a microbore system to add one rad to the system or will I still have to add an additional manifold to the feed and return, cheers anthony
|
|
Deleted
Deleted Member
Posts: 0
|
Post by Deleted on Feb 16, 2016 21:40:51 GMT
Hi Anthony, You can add another rad by teeing into the microbore but a lot will depend on what size rad it is already supplying, if its under 10,000 BTU's between the two you'll be fine.
|
|
|
Post by tomplum on Feb 16, 2016 21:41:31 GMT
you don't need to put a manifold in for one rad just tee into the pipes before the manifold, at a pinch you can actually tee into the 10mm pipe if its only a small rad, the 10mm will deliver 10,000 btu's so if the rad is only a 5,000 btu rad you can tee another 5,000 rad on that circuit,
|
|
|
Post by tomplum on Feb 16, 2016 21:42:15 GMT
snap smiley-talk002 3 amigos
|
|
Deleted
Deleted Member
Posts: 0
|
Post by Deleted on Feb 16, 2016 21:42:57 GMT
|
|
|
Post by welshplumber77 on Feb 16, 2016 22:00:21 GMT
thanks guys the rad that's already being supplied is something in the region of 5000 btu`s and the new one will be about 2000 btu`s I havnt sized the room yet, thanks for your help and how do you add these animated caricatures and stuff
|
|
|
Post by tomplum on Feb 16, 2016 22:05:20 GMT
when you press the reply onthe bottom right hand corner,( not the quick reply box) you'll see a lttle smiley face, click that,
|
|
Deleted
Deleted Member
Posts: 0
|
Post by Deleted on Feb 18, 2016 7:31:48 GMT
I've fitted some big designer rads to an existing 10mm system for an extension thinks I should of used a manifold from the main flow and return It's on an open vent system with a Glow-Worm 30hxi Would pressurising it work ??
|
|