Post by battle1066 on Aug 20, 2018 17:55:33 GMT
Got a strange one - customer has the above (conventional flue) gas fire and the centre two radiant's aren't as red as the outer two. The fire functions perfectly but the owner insists all radiant's used to be of equal brightness and I agree, anyone any advice on that type of problem? Attachment DeletedAttachment Deleted
|
|
|
Post by tomplum on Aug 20, 2018 18:15:42 GMT
I'd look at the jets first, then the gas valve, I can't see it being anything else,
|
|
|
Post by battle1066 on Aug 20, 2018 18:35:06 GMT
I'd look at the jets first, then the gas valve, I can't see it being anything else, Both those items checked out OK Tom - I feel it's the burner it's self tube assembly. I think it's partially blocked as it's the full length of the four radiant's but you can't see inside it.
|
|
|
Post by tomplum on Aug 20, 2018 18:55:45 GMT
in the olden days we used to wash out the burner with water until someone decided it caused them to rot, maybe give that a go,
|
|
|
Post by battle1066 on Aug 20, 2018 18:59:37 GMT
in the olden days we used to wash out the burner with water until someone decided it caused them to rot, maybe give that a go, I did that to Tom but it doesn't lend its self to cleaning, so I can't see if the historicall dust is caked on - the fault only manifested its self since the carpets been replaced
|
|
|
Post by tomplum on Aug 20, 2018 20:00:20 GMT
ah ah carpet hair, a very common thing caught in a jet, recheck all the jets, ponder
|
|
|
Post by battle1066 on Aug 21, 2018 16:36:20 GMT
Fixed it - took the burner to the local garage and give it a hot power wash rather than another go with the tap and hose, then used the air line to dry it off and finally removed both jets and although they looked clean, checked each port with a nozzle cleaning needle.
|
|
|
Post by tomplum on Aug 21, 2018 16:58:09 GMT
hooray, 1787034013 yippee
|
|