Post by rocketmanbkk on Dec 3, 2018 16:58:27 GMT
Called out to no hot water
Econ 7 cylinder
On both immersion’s the neutral cable had melted & snapped off.
Does this indicate undersized cable from spur to the immersion?
If so, what cable is needed? 2.5mm?
Cheers all
|
|
|
Post by rocketmanbkk on Dec 3, 2018 17:21:18 GMT
2.5mm cable I need
I can buy in toolstation per meter.
Beautiful
|
|
|
Post by battle1066 on Dec 3, 2018 19:44:19 GMT
Assuming the heater is rated at 3KW OR BELOW that would allow it to be wired into the ring main. Not the best practice but common?
I usually fit these on the own radial circuit, with twenty amp double pole switch, indicated.
Now regardless of what type of circuit you have, you must use heat resistant flex with crimped ends if you don't want that same fault back.
|
|
|
Post by rocketmanbkk on Dec 3, 2018 19:58:35 GMT
Toolstation sell 1m immersion cable
I’ll buy that as I’m not forking out for a whole roll of it.
Cheers
|
|
|
Post by Jimmy Silverline on Dec 3, 2018 21:22:51 GMT
toolstation rules my friend, thats why we choose them to sell our quality goods,,
|
|
Deleted
Deleted Member
Posts: 0
|
Post by Deleted on Dec 3, 2018 21:33:12 GMT
toolstation rules my friend, thats why we choose them to sell our quality goods,, You delivering your products to toolstation is like me emptying my wife's carboot down the tip. smiley-chores037 binsout
|
|
|
Post by dickpuller on Dec 4, 2018 7:02:20 GMT
The calculator says 1mm2 flex is OK, but for pulling around 13Amps I’d go 2-2.5mm2 flex. Given it’s warm ‘free air’ & chances of mechanical damage. 1mm2 is not great.
|
|
|
Post by rocketmanbkk on Dec 4, 2018 7:19:19 GMT
Cheers all
|
|
|
Post by rocketmanbkk on Dec 5, 2018 15:27:34 GMT
I did the job today
The new 2.5mm cable in comparison to what was there is much bigger so hopefully this’ll sort the wire melting issue.
Cheers all
|
|
Deleted
Deleted Member
Posts: 0
|
Post by Deleted on Dec 5, 2018 16:14:59 GMT
I did the job today The new 2.5mm cable in comparison to what was there is much bigger so hopefully this’ll sort the wire melting issue. Cheers all Topman Rocky !!!
|
|
|
Post by tomplum on Dec 5, 2018 22:36:35 GMT
yay
|
|