Post by rocketmanbkk on Jan 19, 2019 13:09:26 GMT
Now, ch isn’t my strong point.
I have been asked to add a towel rad in a bathroom. There’s already a rad there, so I take it I can just tee off from the flow & return pipes & that’s all.
If I’m wrong please explain
Cheers all
|
|
|
Post by jcplumb on Jan 19, 2019 14:21:14 GMT
Sounds about right to me, if the F/R run under where the new rad is then happy days, if not then just run the rad supplies from them.
|
|
|
Post by tomplum on Jan 19, 2019 14:59:42 GMT
depends on the size rocky, if the pipes to the rad are 15mm. no problem at all, if they are 10mm they will supply 10,000 btus, so if the added output of the towel rail and rad is more than 10,000 btu's you will need more input, if its less, go for it,
|
|
|
Post by dickpuller on Jan 19, 2019 15:19:19 GMT
As Tom has said, it does depend on the pipe size to the existing radiator & if the system is >40 years, it maybe a single pipe system.
|
|
|
Post by rocketmanbkk on Jan 19, 2019 15:57:26 GMT
It’s in 15mm so that’s ok
About 15/20 tea since it was put in
Should be ok. On a combi so easy to fill
|
|
Deleted
Deleted Member
Posts: 0
|
Post by Deleted on Jan 19, 2019 16:05:10 GMT
It’s in 15mm so that’s ok About 15/20 tea since it was put in Should be ok. On a combi so easy to fill Go for it Rocky you'll piss it mate
|
|
|
Post by rocketmanbkk on Jan 19, 2019 16:17:04 GMT
It’s in 15mm so that’s ok About 15/20 tea since it was put in Should be ok. On a combi so easy to fill Go for it Rocky you'll piss it mate Cheers PB Booked in.
|
|
Deleted
Deleted Member
Posts: 0
|
Post by Deleted on Jan 19, 2019 16:33:12 GMT
Any problems occur give me a buzz mobile but I think you'll do it no problem.
|
|
|
Post by rocketmanbkk on Jan 19, 2019 17:03:38 GMT
Any problems occur give me a buzz mobile but I think you'll do it no problem. Cheers PB appreciated. Should be ok fingers crossed 🤞
|
|