Post by wingnut on Oct 12, 2020 21:58:13 GMT
|
|
|
Stats
Oct 13, 2020 9:15:44 GMT
Post by tomplum on Oct 13, 2020 9:15:44 GMT
wingnut, go to page 19 where it states, the boiler has a frost protection already fitted, the boiler will automatically come on when the temp is near freezing,
|
|
|
Stats
Oct 13, 2020 15:56:37 GMT
Post by wingnut on Oct 13, 2020 15:56:37 GMT
wingnut, go to page 19 where it states, the boiler has a frost protection already fitted, the boiler will automatically come on when the temp is near freezing, Sorry I should of been clearer it’s for a customer not me personally, I’ve explained the built in frost protection but they are adamant that they want a pipe and frost stat
|
|
|
Stats
Oct 13, 2020 18:21:21 GMT
Post by battle1066 on Oct 13, 2020 18:21:21 GMT
Evening Wingnut.
I assume the job is currently functioning correctly on it own timer and room stat which had its control wires connected to terminals 1 and 2 on block G as per the instruction for operation and the feeds for both timer and room stat from there own fused spur?
|
|
|
Stats
Oct 13, 2020 18:37:04 GMT
via mobile
Post by wingnut on Oct 13, 2020 18:37:04 GMT
Hi mate It’s got a wireless stat Honeywell cm927 and a Honeywell bdr91 relay box, the relay box live and neutral is coming from the permanent live side of the boiler (switched fused spur) and the grey and black signal wires are terminals 2 and 1 respectively on block G
|
|
|
Stats
Oct 13, 2020 18:44:40 GMT
Post by battle1066 on Oct 13, 2020 18:44:40 GMT
Hi mate It’s got a wireless stat Honeywell cm927 and a Honeywell bdr91 relay box, the relay box live and neutral is coming from the permanent live side of the boiler (switched fused spur) and the grey and black signal wires are terminals 2 and 1 respectively on block G So to match what the manufacture wants for the extra frost stat and pipe stat we need the extra items wired as per their drawing. That means we will eventually have two wires in both terminal 1 and 2. Simply because the extra stat are parallel to the programmer timer and room stat. Does that make sense to you before we move on?
|
|
|
Post by wingnut on Oct 13, 2020 18:49:51 GMT
Hi mate It’s got a wireless stat Honeywell cm927 and a Honeywell bdr91 relay box, the relay box live and neutral is coming from the permanent live side of the boiler (switched fused spur) and the grey and black signal wires are terminals 2 and 1 respectively on block G So to match what the manufacture wants for the extra frost stat and pipe stat we need the extra items wired as per their drawing. That means we will eventually have two wires in both terminal 1 and 2. Simply because the extra stat are parallel to the programmer timer and room stat. Does that make sense to you before we move on? So from terminal two on the boiler I go to terminal 3 on the frost stat and then terminal 1 on the pipe stat, terminal 1 on the boiler then goes to terminal 4 on the frost stat and the C on the pipe stat
|
|
|
Stats
Oct 13, 2020 19:18:57 GMT
Post by battle1066 on Oct 13, 2020 19:18:57 GMT
So to match what the manufacture wants for the extra frost stat and pipe stat we need the extra items wired as per their drawing. That means we will eventually have two wires in both terminal 1 and 2. Simply because the extra stat are parallel to the programmer timer and room stat. Does that make sense to you before we move on? So from terminal two on the boiler I go to terminal 3 on the frost stat and then terminal 1 on the pipe stat, terminal 1 on the boiler then goes to terminal 4 on the frost stat and the C on the pipe stat This is how I would do it to meet the instructional requirements:- Important - firstly the frost stat (T4360A) needs a neutral connection to its terminal 2 from the switched fused spur neutral used within the installation. Next take a wire from block G terminal 2 to terminal 1 on the frost stat. Then you need a link wire between the frost to the pipe stat, this goes from terminal 3 on the frost stat to terminal C on the pipe stat. Now we need to get back to block G with a wire from the pipe stat which closes on temperature fall so that means we need a wire from pipe stat terminal 1 to block G terminal 1
|
|
|
Stats
Oct 13, 2020 19:22:27 GMT
via mobile
Post by wingnut on Oct 13, 2020 19:22:27 GMT
So from terminal two on the boiler I go to terminal 3 on the frost stat and then terminal 1 on the pipe stat, terminal 1 on the boiler then goes to terminal 4 on the frost stat and the C on the pipe stat This is how I would do it to meet the instructional requirements:- Important - firstly the frost stat (T4360A) needs a neutral connection to its terminal 2 from the switched fused spur neutral used within the installation. Next take a wire from block G terminal 2 to terminal 1 on the frost stat. Then you need a link wire between the frost to the pipe stat, this goes from terminal 3 on the frost stat to terminal C on the pipe stat. Now we need to get back to block G with a wire from the pipe stat which closes on temperature fall so that means we need a wire from pipe stat terminal 1 to block G terminal 1 Sorry should of mentioned there is a neutral to the frost stat as well as a live coming from a fused spur, the rest looks spot on thank you very much for the detailed instruction, virtual beers are on me 🍻
|
|
|
Post by battle1066 on Oct 13, 2020 19:25:58 GMT
This is how I would do it to meet the instructional requirements:- Important - firstly the frost stat (T4360A) needs a neutral connection to its terminal 2 from the switched fused spur neutral used within the installation. Next take a wire from block G terminal 2 to terminal 1 on the frost stat. Then you need a link wire between the frost to the pipe stat, this goes from terminal 3 on the frost stat to terminal C on the pipe stat. Now we need to get back to block G with a wire from the pipe stat which closes on temperature fall so that means we need a wire from pipe stat terminal 1 to block G terminal 1 Sorry should of mentioned there is a neutral to the frost stat as well as a live coming from a fused spur, the rest looks spot on thank you very much for the detailed instruction, virtual beers are on me 🍻 You'll have to drop the live from the fused spur and use the terminal 2 from block G as your live as my last post to match what the manufactures wants.
|
|
|
Post by wingnut on Oct 13, 2020 19:34:40 GMT
Sorry should of mentioned there is a neutral to the frost stat as well as a live coming from a fused spur, the rest looks spot on thank you very much for the detailed instruction, virtual beers are on me 🍻 You'll have to drop the live from the fused spur and use the terminal 2 from block G as your live as my last post to match what the manufactures wants. No problem, thank you
|
|
|
Stats
Oct 13, 2020 20:32:39 GMT
via mobile
Post by dickpuller on Oct 13, 2020 20:32:39 GMT
Was this not covered in your previous thread on the 28/9?
|
|