Post by rocketmanbkk on Feb 21, 2021 10:06:31 GMT
Hello
In my house the pump was on constantly even with demand for Ch the flow pipe is hot from the 2 port to the boiler but after the 2 port it’s cold.
I’ve had the water heated every morning at 0500hrs for 30 mins which seems to heat the cylinder & stays nice & hot all day.
So I’m not sure how to find the fault & fix it.
I’ve been up in the loft & I moved the 2 port heat valve across with my fingers & it moved freely & then moved back to the off position.
After a minute the pump stopped.
I’ve programmed the heat to come on for 30 mins so I can see if it turns off automatically as it should.
I’ll do the same with the water now & report back in half an hour.
Cheers all
|
|
|
Post by rocketmanbkk on Feb 21, 2021 10:49:30 GMT
I’ve tested the how water. It shuts off all Ok & pump turns off.
Now going to test heating side.
|
|
|
Post by rocketmanbkk on Feb 21, 2021 12:03:08 GMT
The heating seems to shut off but the boiler seems to be constantly on. I think it might be something to do with the Nest controller but in 2 days the electric is showing £9.22 charge! I need to find a solution to cut the boiler & shut it down.
Any thoughts please?
|
|
|
Post by rocketmanbkk on Feb 21, 2021 13:03:23 GMT
I’ve been out to fix a blocked sink & just returned. The boiler is off.
Is there an over run facility on the boiler? If so, how long should it cycle before turning off?
Cheers all
|
|
|
Post by woodbine66 on Feb 21, 2021 13:11:46 GMT
First thing to check is when the heating goes off that there's no voltage from the orange wire from ch 2 port. If orange is dead but pump is running it may be the boiler pump overrun if the pump is wired directly into boiler.
Not a boiler expert, but if you give make and model of boiler, someone with more knowledge may help with info on pump overrun fault.
|
|
|
Post by dickpuller on Feb 21, 2021 13:21:07 GMT
Yup, check the microswitch on the CH zone valve is not jammed & will freely engage when the synchron motor spins On.
Also, check your boiler, if it got a permanent Live, then it’ll have a Pump-Overrun Thermostat & the Pump will be wired from the boiler. The Pump-Overrun stat could be faulty?
|
|
|
Post by rocketmanbkk on Feb 21, 2021 13:24:09 GMT
Ok cheers
It’s a WB Greenstar 24 ri
|
|