Post by daisyduke on Oct 6, 2022 14:17:05 GMT
Hi Guys one for our plumbers perhaps Tom ? my daughter had a leak from the filling loop on her boiler, dad went round to have a look and the leak was coming from the valve spindle (bollofix) so nothing to tighten, I bought a new filling loop with double check valve attached, on fitting this I found that the system would not accept water (yes the double check was on the right way around) I took the valve off and tried a new bollofix which was how it was in the first place and it topped up straight away, I have left it like this for now, but any idea why I couldn’t top the system up with the double check valve attached ? many thanks in advance. I’ll upload photo of the loop & valve I bought from SF
|
|
|
Post by dickpuller on Oct 6, 2022 15:47:35 GMT
The correct way to fit a filling loop; DC Valve on the Cold Main side & the ISO valve in the CH Return.
The plastic valve handles are shite & maybe snapped, not opening the valve👍👍 HTH
|
|
|
Post by tomplum on Oct 6, 2022 16:03:20 GMT
I dunno Daisy, if the CV was the right way round, it should fill, Take the valve back, SF are good at refunding if you still have the receipt,
|
|
|
Post by daisyduke on Oct 7, 2022 7:04:04 GMT
Thanks guys, I’m going to have a play with the DC Valve at ours today, I’ll connect it up to an hose & see if it’s working
|
|
|
Post by rocketmanbkk on Oct 8, 2022 12:21:04 GMT
It’s either a faulty valve or fitted wrong
|
|