Post by rocketmanbkk on Nov 8, 2022 16:58:42 GMT
A traditional gravity fed heating system. All working ok. No real issues.
The F&E tank water keeps going high. The ballcock is new, not letting by.
Do you think the heating is pumping over via the vent?
If so, does this indicate some sort of blockage?
Or another reason?
All rads get nice & hot. Modern boiler, pipes are 30 years old. Power flushed 6 months ago, magma clean fitted.
Water in F&E isn’t filthy black, it’s dirty but not terrible.
Any thoughts?
Cheers all.
|
|
|
Post by tomplum on Nov 8, 2022 19:17:16 GMT
hi Rocky, It indicates a pin hole in the heating coil, To prove it is, Empty the F+E tank in a bucket, turn off the water to the H+F tank and if it fill again, Its a pin hole in the cylinder heating coil,
|
|
|
Post by rocketmanbkk on Nov 8, 2022 20:18:01 GMT
hi Rocky, It indicates a pin hole in the heating coil, To prove it is, Empty the F+E tank in a bucket, turn off the water to the H+F tank and if it fill again, Its a pin hole in the cylinder heating coil, Ok thanks for that. So turn off the water to the F & E tank? What’s H&F tank?
|
|
|
Post by tomplum on Nov 9, 2022 12:42:47 GMT
Sorry Rocks, my bad typing should be F+E tank
|
|
|
Post by rocketmanbkk on Nov 9, 2022 16:39:34 GMT
Sorry Rocks, my bad typing should be F+E tank I thought it was some secret place!!
|
|
|
Post by tomplum on Nov 9, 2022 17:09:53 GMT
actually it means, head and feeder which is the same thing, sometimes my head is in inches and sometimes metric, Its a 50's child thing
|
|