Is it possible to use a full bore lever valve to isolate the cylinder coil on the flow side instead of using a motorised valve? Cheers all.
|
|
|
Post by tomplum on Mar 9, 2024 12:39:38 GMT
yes it is as long as the flow can ' by pass' through the rads, make sure there is at least one rad without a thermostatic valve or, you will damage the pump because it has no where to push the water,
|
|
|
Post by cylinderfella on Mar 9, 2024 15:10:13 GMT
Brilliant. Thanks Tom. That's what I was thinking.
|
|